TL-PA7017P - cannot connect

This thread has been locked for further replies. You can start a new thread to share your ideas or ask questions.

TL-PA7017P - cannot connect

This thread has been locked for further replies. You can start a new thread to share your ideas or ask questions.
TL-PA7017P - cannot connect
TL-PA7017P - cannot connect
2023-07-29 09:20:43 - last edited 2023-08-29 06:17:48
Model: TL-PA7017P KIT  
Hardware Version: V4
Firmware Version:

I have tried to install the above powerlink in my workshop but it seems my workshop as its own power supply even though it is coming form the mains of the house

 

In the workshop there is a seperate fusebox so is this a different power supply?

 

I can connect both powerlinks in the house but nothing in workshop

 

Please advise or have I wasted my money?

 

Thanks 

  0      
  0      
#1
Options
1 Accepted Solution
Re:TL-PA7017P - cannot connect-Solution
2023-07-31 14:59:10 - last edited 2023-08-29 06:17:48

  @Dale-R 

 

PLC should be connected to the same electric circuit - go through this FAQ - Part 3 for more details on that matter.

If this was helpful click once on the arrow pointing upward. If this solves your issue, click once the star to mark it as a "Recommended Solution".
Recommended Solution
  2  
  2  
#2
Options
1 Reply
Re:TL-PA7017P - cannot connect-Solution
2023-07-31 14:59:10 - last edited 2023-08-29 06:17:48

  @Dale-R 

 

PLC should be connected to the same electric circuit - go through this FAQ - Part 3 for more details on that matter.

If this was helpful click once on the arrow pointing upward. If this solves your issue, click once the star to mark it as a "Recommended Solution".
Recommended Solution
  2  
  2  
#2
Options

Information

Helpful: 0

Views: 291

Replies: 1

Related Articles