GFCI receptacle and HS200 in same box

This thread has been locked for further replies. You can start a new thread to share your ideas or ask questions.

GFCI receptacle and HS200 in same box

This thread has been locked for further replies. You can start a new thread to share your ideas or ask questions.
GFCI receptacle and HS200 in same box
GFCI receptacle and HS200 in same box
2018-07-19 09:59:43
Model :

Hardware Version :

Firmware Version :

ISP :

I'm trying to replace the wall switch with the HS200 but I don't see that the neutral line is connected. Is this ok for the HS200?
Thank you.



  0      
  0      
#1
Options
2 Reply
GFCI and HS200
2018-07-19 14:09:26
Model :

Hardware Version :

Firmware Version :

ISP :

Not sure if my other post went through. I'm trying to replace a wall switch with the HS200 but the switch does not have a neutral wire coming out of it. Do I still need to somehow connect it? If so, so I connect it with the top white wire or the one from the power source to the GFCI receptacle. Thank you.



  0  
  0  
#2
Options
Re:GFCI receptacle and HS200 in same box
2018-07-20 20:45:01
You need the neutral, if you're using a GFCI you must use the line in and neutral from the load side of the GFCI. It's a bit difficult to tell from your drawing but that looks like power through fixture so you need to be careful to wire the switch correctly.