What is the correct load capacity of the HS200 switch?
This thread has been locked for further replies. You can start a new thread to share your ideas or ask questions.
What is the correct load capacity of the HS200 switch?
Model :
Hardware Version :
Firmware Version :
ISP :
I see that the HS200 switch is specified in various places (including TP-Link's web site) as having a capacity of "100-120v, 15 amps" and also "600 watts incandescent". Obviously these two specs are inconsistent, so which is correct?
The wall plugs are consistently specified as 15 amps or 1600 watts, so one might assume that there's a misprint in the HS200 spec, and they meant 1600 watts rather than 600 watts.
But it's also common for devices that use thyristor-type electronic switches to have lower load limits than a relay switch, and they may also be sensitive to the inductance/capacitance of the load. The term "incandescent" is often used as a shorthand to mean "resistive load" since an incandescent bulb is a pure resistive load, whereas florescent and LED bulbs may present capacitive/inductive loads. This term's presence suggests that the HS200 might be such a switch, in which case it could be the 15 amps that's wrong.
Hardware Version :
Firmware Version :
ISP :
I see that the HS200 switch is specified in various places (including TP-Link's web site) as having a capacity of "100-120v, 15 amps" and also "600 watts incandescent". Obviously these two specs are inconsistent, so which is correct?
The wall plugs are consistently specified as 15 amps or 1600 watts, so one might assume that there's a misprint in the HS200 spec, and they meant 1600 watts rather than 600 watts.
But it's also common for devices that use thyristor-type electronic switches to have lower load limits than a relay switch, and they may also be sensitive to the inductance/capacitance of the load. The term "incandescent" is often used as a shorthand to mean "resistive load" since an incandescent bulb is a pure resistive load, whereas florescent and LED bulbs may present capacitive/inductive loads. This term's presence suggests that the HS200 might be such a switch, in which case it could be the 15 amps that's wrong.