hs210 configuration usable?

This thread has been locked for further replies. You can start a new thread to share your ideas or ask questions.

hs210 configuration usable?

This thread has been locked for further replies. You can start a new thread to share your ideas or ask questions.
hs210 configuration usable?
hs210 configuration usable?
2019-09-02 22:29:13 - last edited 2019-09-03 22:57:39
Model: HS210  
Hardware Version: V1
Firmware Version:

I have power coming in through the light

From the light is a two wire cable going to the first switch box

From the first to second switch box is three wire cable

 

The neutral from line in is connected to the light fixture neutral

The hot from line in is connected to the white going to the first switch box, it is spliced with the white going to second switch box, and there it is connected to the second switch common terminal.

The hot connection for the light is connected to the black going to the first switch box, and there it is connected to the first switch common terminal

the red and black of the three wire cable are connected to each switch's respective traveller terminals.

 

Is there a way to use the HS210 three way switch?

 

  1      
  1      
#1
Options
1 Accepted Solution
Re:hs210 configuration usable?-Solution
2019-09-03 00:29:07 - last edited 2019-09-03 22:57:39

You do not have a neutral in either switch box, so the HS210 can not be used.

Recommended Solution
  0  
  0  
#2
Options
3 Reply
Re:hs210 configuration usable?-Solution
2019-09-03 00:29:07 - last edited 2019-09-03 22:57:39

You do not have a neutral in either switch box, so the HS210 can not be used.

Recommended Solution
  0  
  0  
#2
Options
Re:hs210 configuration usable?
2019-09-03 20:44:33

I was afraid of that.  The second switch is in a gang box with another switch on a different circuit.  Can I tie the hs210 neutral in to that, or does it have to be on the same circuit as the light it is switching?

  0  
  0  
#3
Options
Re:Re:hs210 configuration usable?
2019-09-03 22:33:21 - last edited 2019-09-03 22:34:52

It is against code to use neutral from a different circuit

  0  
  0  
#4
Options

Information

Helpful: 1

Views: 1202

Replies: 3

Related Articles